Sorry for delay...
Ok, now we have 12 out of 16 PLC's not working on a network.
This would lead me to believe that something is different between the 4 working ML1400 and the 12 non-working ML1400?
kapil.29jha said:
PLC
CAT: 1766-L32BWA series A Frn 5
IP: 192.168.1.15 to ...30
Subnet: 255.255.255.0
Gateway: 192.168.1.100
Are all 16 MicroLogix 1400 definitely series A
Frn 5?
Have you personally checked them all online?
If you are not sure, go online to each 1400 using serial, and go to:
"
Processor Status", "
Proc" tab, "
Processor FRN S:62 = x.x"
(See attached screenshot)
I'm wondering if the 4 working 1400 are
FRN 5 and the other 12 are
FRN 4 or lower?
Do any of 1400's fault when you try connect via Ethernet?
kapil.29jha said:
...when i try to resolve problem on one PLC (one by one) i got that the plc is not communicate via ethernet port where as it comunicate with serial cable perfactaly.
i change the perameter for ethernet communication and agian try to communicate but no result...
When you say you "change the perameter", what exactly are you changing and where? Is the static IP address you assigned reverting to 0.0.0.0?
There is an anomaly with the MicroLogix 1400 Series A
FRN 4 or lower, where a brand new MicroLogix will fault with 08h error - "internal software error" after assigning a static IP address, and connecting an Ethernet cable
before power cycling to enable the IP address. FRN 5 fixed this anomaly.
IF any of the 1400 are at FRN 4 or lower,
To check for this issue:
Leave Ethernet cable
unplugged.
Go online to one of the FRN 4 or lower 1400 using serial.
Assign the static IP address, etc.
Power cycle the 1400.
Then connect the Ethernet cable and try to connect.
If this is your issue, updating the Firmware to FRN 5 will solve this issue permanently.
If they are all indeed FRN 5, forget the above and we'll try move on.
EDIT: I forgot to ask if they had been working for some time, or is this a new installation?
G.