I can't see Mickey's figure, so this may be redundant.
This is essentially a thermostat, that is, floating point control. You have a lower limit and an upper limit, where the upper limit is the lower plus your deadband or error tolerance. Scale the T/C input as real temperature, degrees F.
Use two comparison statements. If the actual temperature is less than the lower limit then turn on your contactor. Use a holding contact to keep it on until the actual temperature is greater than the upper limit. Then turn off the contactor by dropping out the holding contact.
You can add refinements to keep from chattering if hte measured temperature responds very quickly - time delays that don't turn on the contactor until the temp is low for a set period, and a timer to inhibit the contactor coming back on for a set period.