I need help in programing a evironmental chamber to vacuum and back fiil with gas (Purge).
In the first 3 hours,
Vacuum to 150 Torr
Purge with gas to 650 Torr
Repeat the above for a total of 3 times
Then maintain Pressure at 650T until the 3 hrs are up.
In the next 7 hours,
1. Vacuum to 150T
2. Purge to 650T
3. Wait 10 minutes
4. Vacuum to 150T
5. Purge to 650T
6. Wait 10 minutes
7. Vacuum to 150T
8. Purge to 650T
9. Full Vacuum for 30 minutes.
Repeat the above steps 1 thru 9 for a total of 3 times
After 7 hrs,
10. Purge to 650T
11. Vacuum to 150T
12. Purge to 650T
13. Vacuum to 150T
14. Purge to 750T
The Inputs ares:
I0:0.0/0 Start Mon Push Button
I0:0.0/1 Reset Program Mon Push button
I0:0.0/4 Program Selctor swicth
The Outputs are:
O0.0/0 Vacuum Vavle
O0:0/1 Purge Vavle
O0:0/2 Cycle One lite
O0:0/3 Cycle two Lite
O0:0/4 Cycle trhee Lite
O0:0/5 On lite
O0:0/6 Purge Lite
O0:0/7 Vacuum Lite
You've made an excellent start by defining all the steps in the sequence. It appears that you need sensors to indicate when the chamber is at 150, 650, and 750 Torr.
This could be a good application for a sequencer instruction if your PLC brand supports it.
Do you have a specific question?
Your project looks like a natural for a drum timer. Some of them are easy to work with - AutomationDirect.com for example. Others are difficult to set up and use.
To get you started, you can also consider using counters in conjunction with timers to keep track of which step you are on.
Do u use any pressure sensor to detect the vacuum pressure as your requir setting(150T, 650T & etc).If u are using a sensor which is an analog output then you need an analog input card to do the sequence u want. I think s7-200 series have the analog card u need.
Using Micrologix 1000 Analog and RSlogix 500
Have solved the analog input and scaled it to represent the pressure.
Store it in register N7:1
Just need help in doing the sequencing of these events
Sequencer
Here is a link to some sample sequencer programs.HERE
I agree with Tom Jenkins that a drum timer on the Automation Direct plc would be easier.
Well Mike It looks like you have every thing in hand,
Here is a simplified version of what I do in sequencers.
Hope this gives you the peice you are missing.
Hi, first time poster just wondering if anyone has any tips for a novice of the PLC world, I've worked with them a fair bit within schooling and...
3,262
We're a used machinery merchant and have a Siemens PLC that has lost its program due to a dead battery. We have the software to download but, at...
22
6,639
Hi I’ve got a door and window switch from RS (190-1011) with a 4 core cabl - red, white, green, and yellow . The red and white are the switch and...
1,360
I'm self taught so far, so hang with me as I try to explain my issue. I've got an archived program file for a PVP6 that I'm opening on FT ME ver...
2,598
If 95% of our PLCs are AB (micro 1500, slc5/03,04 make up the bulk) what would be the language to learn to use scripting? Also to move towards...
2,166