number entry to control a pid
stu
Aug 2005
England
785
hi i have a ML1200 (ab) plc how can i use a number entry display to enter the setpoint in a pid? the pid has an transducer to control the speed of a pump, the setpoint is in pressure please help
If your data entry device does not support writing directly to the pid file you could wtire it to a "n" file then use a move instruction to move it to the pid file.
hi say i am using a pid (pd10.0) to add the setpoint from the hmi to the pid do i instruct it pd10.0/sp am i right ???
First question: Do you now have a functioning PID loop?
2. Do you have a means of entering the setpoint?
3. If question 1 is a yes, can you post a snippet of the PID setup?
This is pretty straight forward, but there a lots of details, and posting your PID setup will allow us to assist you, without having to play 20 questions.
Ken
at the moment i am starting to write the program, i have not got the pid set up yet. i have got a entry on the hmi for the pid but i need to address it? is it like addressing a timer by putting eg /dn on the end but instead use a sp(setpoint on the end of the instruction)
You don't say what software you are using. For RSLogix 5000 I create a tag Loop#_SP. In my function block program I select the tag and connect it to the PID function.
You are correct though, you can probably address it directly
Roy
sorry i thought micrologix 1200 could only be programmed by rslogix 500. (i am new to plcs)thanks stu
Stu,
You may be right, I don't claim to be an expert on AB products, it's just that I have been using 5000 lately.
I don't have 500 at the moment.
Roy
Stu,
You were right, RSLogix 500 is the only software for programming the Micrologix 1200. In order to answer your original question, what are you using for the operator interface?
PID Example
Stu:
This is an example of PID for a ML1200, in this case the setpoint is taken from N7:3 ( Thermocouple Type J range), in my example this value is entered thru a PV300, your case is the same but different brand.
Observe the scale for PID and observe where the scaled value is written.
PV data is scaled for PID also (I:1.0)
I am working with a company that wants to package all of their Rockwell software for automated deployment through the IT infrastructure. This...
19,129
When I use the Data Entry to enter a new number, a keypad pops up on the display. This Keypad is rather small. Is there a larger one available?
3,179
Hi ! I have a big problem in my PanelView project. I have to build a production report into an Allen-Bradley project into a PV600. Operator...
3,130
I am working on a project using a NB screen and NX1P2 PLC. I am having a really hard time getting a real number to properly translate through to...
134
Complete noob here, using a Click C0-02DD1-D to run a test stand. Requirement is to turn on motor run for X seconds, turn off and dwell for X...
1,106