OB86 wont download

cjd1965

Lifetime Supporting Member
Join Date
Apr 2007
Location
UK
Posts
1,659
Hi
My PLC wont accept OB86,but the simulaor will

It is a 6ES7-315-2AG10-0AB0 /V2.0

OB86 is actually 'empty' of code. The config is basically about 8 i/o cards and a cpu

Any ideas? I am trying to detect hardware faults

Cheers
 
hello cjd;
What happens when you try to download OB86 to your real CPU?
Any error messages, system messages?
This would be very strange, as the diagnostic OBs are always accepted on every Siemens CPU. Even empty, they still serve an important purpose (they allow the bypass of a specific error situation so the CPU does not enter STOP mode on this error, and provide information on the source of the problem to the diagnostic buffer).
Please tell us more.
Hope this helps,
Daniel Chartier
 
I wont have access to the plc until after christms now. Other problem was some fc's wouldnt go but if i opened them and did them from the editor with no edits they would download...pain in the a$$
 
Hello

You can only download OB, SFCs and SFBs if your CPU supports them. You can have information from the manuals which OBs your CPU supports.

In this case your CPU doesnt support OB86 which means if you have a problem with your rack your CPU wouldnt be able to see it.

I am not sure but OB86 is for S7-400 series because S7-300s doesnt have an electronic backplane.
 

Similar Topics

Hello.We are using S7-300 Cpu.Sometimes give an error.OB86 and OB122 blocks called.OB86 Block ; L #OB86_FLT_ID T...
Replies
7
Views
1,930
I have a S71200 PLC connected to GSD board as a ProFinet I/O I am tasked with detecting when loss of communication happens I understand this...
Replies
2
Views
2,754
Hi, lets say that wehave one S7-1500 and one ET200S connected through profibus. I remove profibus connection from ET and detect a problem using...
Replies
1
Views
1,979
Hello, I'm working with OB86 to track some diagnostic data, i write all start information of the OB to a DB including the timestamp. but when i...
Replies
4
Views
5,184
We have S7 414-H PLC. In the software I found Organization block OB82. But in the network nothing code there.. Comment is there I/O fault 1. And...
Replies
8
Views
8,687
Back
Top Bottom