Hello.We are using S7-300 Cpu.Sometimes give an error.OB86 and OB122 blocks called.OB86 Block ;
L #OB86_FLT_ID
T DB1.DBB 14
L #OB86_EV_CLASS
T DB1.DBB 15
L LB 11
T DB1.DBB 16
When I looked to DB1.
DB1.DBB14 : Byte: B#16#C4
DB1.DBB15 : Byte: B#16#38
DB1.DBB16 : Byte: B#16#5
And in OB122 Block:
L #OB122_MEM_AREA
T DB3.DBW 14
L #OB122_MEM_ADDR
T DB3.DBW 16
When I looked to DB3.
DB3.DBW14 : Int:16
DB3.DBW16 : Int: 4
is showing.And we make plc stop/run.Maschine is run and operating again.
According to these values can we fix problem.That is which module is defect?
Thanks in advance.
Parky, thank you for your kind return. I understood the working philosophy of OB86. It shows that there is a problem with the station with the Profibus address of 5.
It shows integer 16 as #OB122_MEM_AREA, integer 4 as #OB122_MEM_ADDR. I don't understand if this address is DI or DQ module address, bit, byte, word, dword access? Thank you for any additional information.
If you have come so far as to identify DP station #5 as the culprit, then looking into the diagnostics buffer wont help any further.
You need to troubleshoot the issue by checking the hardware.
Check the cables and connectors.
Check earthing and equipotential bonding.
Swap the station #5 with another identical hardware. Does the problem disappear, remain, or follow the swapped hardware ?
Parky and jespermp thanks. I changed the profibus connector of station no.5 but the fault continues. So i replaced all profibus cables and connectors of the machine. The machine works without problems for 1 week.
Yep it's the most common problem I have come across, had a number of failures on cable or connectors (even had the termination resistor switch go open) that is used on the ends of the profibus run.
Yup, cable & connectors are the most common issue I've seen with Profibus, other than someone moving the switch "accidentally" and a pretty regular failure we saw with a Festo bus module.
Hi everyone. I have an S7 313C-2DP, connected to another siemens through a DP/DP coupler. The coupler is powered from the other plc. When they...
10,291
Hi i using Kinetik 300 2097 driver control by EIP with using move absolute and incremental for motion , but i want to add same driver and motor as...
41
41
Hi Siemens guys! I am experiencing SF fault on our S7-300 (6ES7 315-2AH14-0AB0) CPU from time to time. I've checked the diagnostic buffer and...
178
Have a system that has been running for over a year and all of a sudden getting a ExcessiveVelocityFault on one of the drives when the MSO command...
148