omron ch200he I/O unit

ajay34

Member
Join Date
May 2010
Location
klang
Posts
249
hai all ..

i been working with omron 200HE for some old system ..
where by i have 2 spare input module and 3 spare output module..

since alot safety item are in ..i seem lack of input module..

can i put input module on output module backplane..

my meaning is input backplane is full from channel 0 to 9 .
and out backplane have 1 more spare..
if can what i need to do or any configuration i need to make
 
Yes - anywhere. The addressing will be after the last output card. If you are using 16 bit cards the channel address will be 10.
 
thanks for the info ..but i m curious coz on id it show chanel 0 to 9 follow by a,b,c & d
mean i have to set the chanel after the last input id no 9 ..it should be A is it correct.
 
hai..i try to upload from current plc .I/O table but i got msg saying there no setting for the on plc..and when i put in input module on out rack it show error ..read the error was saying
I/O was over something ..last input module i set as chanel A
 
You have to go online, put the PLC in program mode and create the I/O table.
 

Similar Topics

hi all... :bow: i having porblem to online with c200he omron plc.. recently 1 bought software CX program v.9 ( omron) and GX v.8 for...
Replies
23
Views
4,114
:bow:... hello guys ...i been having problem with omron CPU CH200HE..where the red led error light is on ..but it not flashing ..it continue...
Replies
5
Views
2,104
I've come across a system running omeron cx-programmer version 9.42. Am I going to need to find a legacy version of the software to edit and...
Replies
1
Views
67
Has anyone done SMS messaging from an Omron CJ2J-CPU31 PLC? If so could you help please. Omron here in Oz have not had any experience doing this...
Replies
5
Views
199
I have an old plc in the system I have, moxa nport was used to communicate with scada, I want to replace the plc with cj2m cpu33 and eliminate...
Replies
1
Views
78
Back
Top Bottom