Omron CJ1W-CIF21 simple comms unit
RoTaTech
May 2003
Cobourg, ON, Canada
418
First, my jab - simple communications unit - yeah right. That must mean that it is simple - as in simpleton, not simple to use.
Point:
I am using an Omron CJ1M, with this CIF21 attached. There are 21 identical temperature controllers linked to the CIF.
I am modifying a network and program. The original program was written for 17 TCs, and 4 more were added. They are configured correctly as far as wiring, remote access enabled, etc.
I modified the existing program to read and write the new controllers, by replicating the existing controller logic. All we do is read and write 4 values, setpoint, present value, hysterisis, and on/off status.
I can read from the new and old controllers, so I know I have the addressing correct, and at least the read logic, but I cannot write to them.
The data goes into the DMs that should be sent to the TCs, but does not update the TC itself - either on the read data (i.e. if I write a new setpoint, I should be able to read it back), nor on the TC itself.
Any ideas? Has anyone else ever used a CIF?
I have not used the CIF21.
Have you checked the manual?
You should be able to download from:
www.omron.ca choose Document Library from menu on left.
Enter W400 in partial document number box, then search.
Hope this will help.
Reference manual section 4-2.
Guessing the problem is setting for number of connected units.
Hope this helps.
got the manual, got a 'quick-start' guide written by Omron tech support in Toronto, still no luck yet.
They think it may be a timing issue where the CIF is not given enough time to update all the controllers, but do not have a definitive answer.
I have PLC Omron CJ2M with OD211 module. I want to use the pulse output and PWM output and this module. But i confuse how to activated this, i...
114
Good. ,how to connect the relay outputs to the CJ1W-OC211 card ?
1,166
Hello everyone, I would like advice on the setup below: CJ2M PLC: 192.168.10.01 (Subnet: 255.255.255.0) ETN21 - 192.168.20.1 (Subnet...
1,866
Hello, I have an installation with an omron plc CP1L with a CJ1W-CIF12 module connected to eight omron MX2 drivers. I use the bus to modify the...
2,147
Hello all, has anyone configured before 2 CJ1W-ETN21 in a single rack? I am trying to put 2 units of ETN21 couple with my CJ2M-CPU33 to act like...
1,275