Omron cqm1 cpu45-v1 problem

Kareemhammad

Member
Join Date
Aug 2014
Location
Egypt
Posts
5
Hello
So we have an orange sizer that uses omron cqm1 cpu-45 the problem is the sizer was stored for so long and there is a chance the plc was dropped or hit several times
So now my boss wants it to work again i connected everything appropriately the mechanic parts work perfectly the problem is in the plc and the computer
The computer says no plc connected and the plc has a led called com2 where the rs232 connected to the computer and it's not on it's always off i'm sure i connected the rs232 correctly as the manual says
Anyone could help me find the problem to make the com2 led on!!!!!?
Thank you
 
Make sure you are using the correct cable.
The Omron 9 pin is not a standard pinout.
Also check the DIP switches on the cpu.
Please see attachments.

CQM1_DipSwitch.jpg
 

Attachments

  • GTC99CC.pdf
    8.5 KB · Views: 11
It's also work mentioning that the CQM1 is particularly sensitive about working with USB/serial adapters. It is best to use a built in COM port on the PC or an expresscard RS232 adapter.
 
Oh i forgot to tell you there is a screen connected to the omron cpu and it's broken is it a problem or i could work without it ???
 

Similar Topics

Hi to everyone, I need little help with above mentioned CPU which was faulted few days ago. I have managed somehow to clear memory fault...
Replies
5
Views
4,401
Hi! Has someone a pinout and/or wiring diagram for an old CQM1-CIF02 cable? Thanks!
Replies
2
Views
1,907
Hi; I have a DUPONT brand machine having OMRON PLC CQM1-CPU21-E. I have CX Programmer installed in my Laptop having W1indow10. I want to go...
Replies
10
Views
3,613
Dear All, Does anybody knows Omron CQM1 0ch Module details?? or manual i try to search but cant find manual or complete order code if this...
Replies
4
Views
2,373
Hi, I've been asked what is involved to upgrade and old CQM1-21 Omron PLC to a CJ2M. I have the old file with an extension of .cdm and searches...
Replies
3
Views
1,587
Back
Top Bottom