I need some help getting the TC102 module working. I want to ON/OFF regulate, and the transmitter is a PT100. When W0.00 (se picture below) is high i want to on/off regulate around the setpoint 80`C. Output 1 goes high/on when the PV temperature is below setpoint.

When w0.00 is low, i want output 1 to go low/off. I have read the manual and are aware of the DIP switch settings. But does output 1 go OFF in the program below when W0.00 gos low ? Are there more i have to consider to get the regulation started ?

ScreenShot002.jpg
 
Do not know the card but would imagine so. Hopefully someone who knows the card will come online for you.
 
You need to control bit 2022.06 to stop the output.

Turn OFF the Stop Bit to perform temperature control for loop 1
and turn it ON to stop temperature control for loop 1.
The Stop Bit will not function if pin 1 on the DIP switch is OFF
and the CPU Unit is in PROGRAM mode.

Its in the manual W396-E1 page 35.
 
thanx for all you`re help. I have downloaded the manual, and are wondering if it is a typing error in it. Section 3-7 says about the setpoint:

" To change the loop 1 set point from 0 to 200°C, write a value of 0200"

But section 3-8 says:

" Set the loop 1 control sensitivity to 2°C in DM word m+14 (Set D (m+14)to 0020 "

So the setpoint, 200`C = 0200, but the control sensitivity 2`C = 0020 ? Do they mean 0002 ?
 

Similar Topics

Please suggest me programing cable for omron plc sysmac model no. Cpm2a
Replies
1
Views
1,139
Hi All, Can anyone tell me if its possible to program an Omron CS1G-CPU43H via an inserted CS1W-SCB41-V1 2 port communication module, on port 2...
Replies
5
Views
2,421
I am trying to scale my analog input from 1-5V to 0 to 1000. My parameters are D290 D290 + 1 = 0000 D290 + 2 = 0064 (1V) D290 + 3 = 1000 D290 + 4...
Replies
9
Views
4,157
Hi, I did a search forthis on the site and found a link to page 1728 but not post about this??? any answers? Thanks, Steve
Replies
3
Views
7,390
hi all, Is there some one there to help me out for this interesting omron logic?? the thing is that let us assume that i have D0 to D5000 memory...
Replies
4
Views
4,491
Back
Top Bottom