Omron TIM
Andy Veitch
Oct 2012
Oxfordshire
26
Trying to get my head around the TIM instruction on a Omron CP1E plc.
The maximum set valve is 9999 which is only 9.9 seconds. (BCD )
What if I want a timer to run for 4 hours ( 14400 sec )
What can I use ?
Can I change the timer base from milliseconds to seconds?
Please tell me there is another timer I can just type the amount of seconds into.
Regards
Andy
The TIM instruction is actually a 100mS timer so would range up to 999.9s. Alternately you can use the TIMX instruction which utilizes the Binary range (rather than BCD) up to 6553.5 sec. But that doesn't answer your need for a 4 hour timer.
I've never been real fond of the TIML instruction for long time periods. I prefer to roll my own using the P_1s (CF102) or P_1min (CF104) system bits to increment an integer.
Hi Moggie,
I don't seem to have the option of the TIML.
I have the following TIM or TIMX.
I've got a feeling I am going to have to use a 1 second counter.
Andy
On a Omron timer in BCD mode, counts are incremented every 100mS.
So that's 10 counts a second. Check out the Omron programming manuals or instruction help file for more details. They explain it very well.
The TIML(553) instruction is supported for the CP1E using CX-Programmer v9.6. Not sure why you would be having a problem using it.
Not a fan of TIML - restrictions. Use a 1 second or 1 minute pulse into a counter. Easiest way for mine.
OK, I can see where I've gone wrong. it's actually number of 100msec counts that you enter not actual millisecs.
Thanks for explaining that.
Andy
Another approach is to have a scheduled task that runs once every second (or minute) based on the internal clock bits P_1s or P_1min. With a task of this type you can do whatever is needed at a fixed interval.
I have an older CQM1H-CPU21 with cs-programmer 4.0. I have a TIM instruction and I'm trying to lower the time. The value for the timer is stored...
2,210
hello to all I set a timer in omron plc(CPM2A) to count seconds but I have problem here!! time in omron plc is faster than I expect ! I know TIM...
3,174
Has anyone done SMS messaging from an Omron CJ2J-CPU31 PLC? If so could you help please. Omron here in Oz have not had any experience doing this...
145
I have an old plc in the system I have, moxa nport was used to communicate with scada, I want to replace the plc with cj2m cpu33 and eliminate...
63
Hi all, i have 8 CJ2m plc units that show different numbers on the plc display and i am stuck on reading the info. my unit has an ip address of...
102