OT: Short circuit rating confusion
rQx
Oct 2010
Trelleborg
1,051
If you aren't sure what Type 2 coordination is, take a look here:
https://www.schneider-electric.us/en/faqs/FA105974/
Basically, what the chart is telling you is what maximum amperage general purpose fuse you can use in combination with each size switch and still achieve the high fault current rating listed in the table.
As an example, assume you are using a 32A rated switch. According to the table, as long as the circuit is protected with a 35A or lower fuse the short circuit rating of the switch is 15kA. If you had a 40A fuse protecting the circuit the short circuit rating would drop to 5kA.
Keith
Also note that the first value, SC rating = 5kA, is per UL rules.
The "Short circuit current (co-ordination type 2)" is an IEC rating, and it is only in series with fuses, specifically type g or G.
This is going to be the same for all non-fused switches of this type. They are made to go near the motor as a safety disconnect / isolator, but must be used in coordination with some other upstream Short Circuit Protective Device that limits the fault current.
Thanks for clarification, it doesn't clearly state that to 5kA is UL. Tricky with both UL and IEC in the specs.
I have another issue with a 100-c contactor. If I interpret this correct then if I fuse a 100-c16 contactor with max 50A gG fuse then it can handle 50kA type 1? The headline says fuse or circuit breaker rating but the options are only fuses.
Page 54 https://www.google.com/url?sa=t&sou...FjAAegQIBBAC&usg=AOvVaw1tvhRcF3rKg8EWvT5mKsLU
Also this fuse will be before the whole cabinet in the supply end but I guess that doesnt matter then , what matter is that the fuse is correct size
I read the chart the same way. For a 100-C16 contactor you could have up to a 50A gG class fuse and still have a type 1 coordination short circuit current of 50kA for IEC purposes.
Keith
Hi all. I've been looking at the latest version of UL508A, and am finding that my understanding is basic, at best. What I've been trying to find...
8,200
Hi group! Repeatedly found answers to some questions in the PLC's programming world, now I decided to ask the question directly) Now I am...
22
4,243
Hi, I'm a little bit confused on how understand the short-circuit ratings on some components in my cabinet and hoping for some advise. I have...
1,928
Hello, I have a customer with a ABB ACS601-0025-2-000B1500001. I cannot seem to find a good troubleshooting manual online. This is one vfd...
1,405
I'm looking at Profibus DP repeaters, and have been reading datasheets and user manuals. The website for the Procentec model B1 repeater refers...
1,478