OTE stuck on with false rung

boomdoom86

Member
Join Date
Jul 2014
Location
Ohio
Posts
12
I'm working with a 1764 Micrologix 1500 series C with RSLogix500 V9.00. I had to add some features to a purchased machine to facilitate new product models, the project quickly got out of hand. To make the program more readable, I created a series of the conditional bits for the features I added in a new subroutine.

I'm having trouble with some OTEs that are remaining energized, not only when the rung condition is false but also when the subroutine is not being scanned. These bits only have one output instruction and are not controlled by and HMI or other external device.

See attached files to note that LAD 21 JRS not being executed and LAD21 rung false for B3:7/5.

Does anyone see a mistake or have input on this matter?

JSR not being executed.jpg Non-Scanned Sub OTE.jpg
 
Last edited:
If you don't scan a subroutine, you will never evaluate the logic which tells the OTE to turn off, the OTE will remain in its last state. This is normal behavior.
 

Similar Topics

I have a PanelView Plus on a machine that we had a contractor make for us. After the operator inputs their username, it gives an error saying that...
Replies
7
Views
3,797
Something I've never thought about before... maybe you folks have some thoughts or experience. I have a customer that uses a Weidmuller, Modbus...
Replies
0
Views
30
Hi, We have been facing a issue with SCADAPack 474. Configuration is like below. RTU 474 + 6103 PS + 5606 IO Mix Module + 5414 DI Module Only...
Replies
0
Views
72
Hello, Can anyone recommend an expandible IO module with OPC UA? I've deployed the Emerson RSTIO-OM module and it works great, but it has a...
Replies
0
Views
53
So I'm pretty new around here but I come looking for advice or suggestions to research. Im the plant electrician/SCADA guy for a warer department...
Replies
8
Views
290
Back
Top Bottom