Outdoor temperature compensation for silo heating

RonJohn

Lifetime Supporting Member
Join Date
Jul 2013
Location
NE Ohio
Posts
535
I have a pair of outdoor uninsulated water silos that need to be maintained at or above 145°F. Both are supplied by the same source, which includes a heat exchanger for pre-heating. That same heat exchanger can be used for recirculating one silo at a time. This is a new piping arrangement to coincide with the temperature requirement.

We've had some cold nights around here as winter's approaching and my silo temps haven't been able to keep up with the outdoor temperature drop. It only got down to the 20s so far and last winter we hit just south of -20°F once. Does anybody know of a good formula/correction factor to compensate for outdoor temperature in such a situation?

I'm using Peter's SMC algorithm to control the steam and it's worked great for months, so I don't think that's an issue. It seems like I simply need to be more proactive in accounting for the cooler nights.

Thanks in advance.
 
I no longer have the formulas handy, but if you look at some HVAC resources for optimized stop/start it should give you some factors. If memory serves me right the function is non-linear, but for your purposes you may be able to linearize it and get adequate results.

To tell the truth, unless the steam is free I'd think insulation would be pretty cost effective!
 
Thanks Tom, I'll see what I can look up.

To tell the truth, unless the steam is free I'd think insulation would be pretty cost effective!
Good thought! Somebody else couldn't justify the cost of an insulated silo (almost double, I'm told). Not sure how it'd work to insulate a silo after the fact. Maybe we could just put a "stocking cap" on top... o_O
 
I have a pair of outdoor uninsulated water silos that need to be maintained at or above 145°F. Both are supplied by the same source, which includes a heat exchanger for pre-heating. That same heat exchanger can be used for recirculating one silo at a time. This is a new piping arrangement to coincide with the temperature requirement.

We've had some cold nights around here as winter's approaching and my silo temps haven't been able to keep up with the outdoor temperature drop. It only got down to the 20s so far and last winter we hit just south of -20°F once. Does anybody know of a good formula/correction factor to compensate for outdoor temperature in such a situation?

I'm using Peter's SMC algorithm to control the steam and it's worked great for months, so I don't think that's an issue. It seems like I simply need to be more proactive in accounting for the cooler nights.

Thanks in advance.

This sounds interesting, although I just breezed through the link that you provided regarding the control. So I'm guessing your using steam with an on/off valve vs. a modulating valve?
 
That's correct, DG. We didn't have any analog outs available on this PLC, so SMC has worked well, although I had to fudge the time constant.

A cursory search turned up one webpage that hinted at a 1°F setpoint increase for every 7°F outdoor temperature decrease with no supporting math. This is more than double what I'm currently doing. I'm finding lots of other sites that talk about how modern day HVAC controls have this optimization built in, but no factor/algorithm that I can follow.
 
Good question. Each silo has a temperature transmitter mounted near the bottom of the silo.

Additionally, the supply pipe comes in about 15 feet, which is roughly half way up the silo wall. Since heat rises, I do tend to see an overshoot once the temperature catches back up. We're talking 30k gallon silos so the water is hanging around in there for a while as we try to keep them at least half full.

This is not the ideal situation but if it were easy, anybody could do it - right?
 

Similar Topics

Good morning :site: For the past few days, I've been struggling with getting an accurate reading of the outdoor temperature. Parking lot on...
Replies
10
Views
2,693
Was wondering what is everyone using for outdoor rated OIT/Panel View covers? OIT is mounted on a panel. Shade would be preferred as the panel is...
Replies
2
Views
1,202
I need a small HMI or numerical keypad to communicate with a Click PLC to enter a 4 digit number. It'll be mounted outside but under a canopy and...
Replies
3
Views
1,848
Just wanted to see if anyone has any experience with an outdoor HIM/HMI with a window (see example on website here) Outdoor VFD HIM example? We...
Replies
4
Views
1,774
A little OT but there will be a PLC in some of these... :) I'm looking for insulated instrumentation cabinets for summer and winter, freeze to...
Replies
13
Views
2,375
Back
Top Bottom