PanelView 1000 FT View Studio - Child Page with Parameter List

moistcat

Member
Join Date
Jun 2020
Location
Melbourne
Posts
54
Hi All,
I was wondering if it is possible to use parameter files that can be passed to a second page eg:

--HOME
---PUMP 1 FACEPLATE (With Parameter List - Opened from HOME)
------PUMP 1 SETTINGS (With Parameter List - Opened from Faceplate)

Cheers,
 
Yes, parameter files or parameter lists will pass (carry forward) parameters from one display to other related displays that are opened from the initial display.

To carry the same parameter forward to subsequent displays, assign the same tag placeholder (for example, #1),
instead of a tag name in the parameter list or parameter file field of the object in the related display.
 
They can also replace part of a tagname or a folder.
You can pass "PP1" for a pump and then add the reset of the tag on the Child screen. IE #1_Start or #1_Speed etc. Or for if you have each machines tags in a seperate folder you can pass "Machine1" and then use the tags like #1\Start_PB


You can also just pass strings or absolute values.
 
How do I actually call the related page?
Im using the Goto Display Button.

Image 1 is the dynamic page called with Parameter List (from the main menu).
Image 2 is the sub page, called form the above page.
Image 3 is my Goto display button props.

vmplayer_XfWRFHGBpj.png vmplayer_kOt9rPunDi.png vmplayer_M3fXEA5udD.png
 
In my experience, you have to use parameter lists, not parameter files, for this to work.

Edit: to clarify, in the goto display config screenshot, you're looking for a parameter file called #1. You should be passing #1 in as a parameter in a list
 

Similar Topics

Hello, I made a change in alarm setup in factory view studio, where I changed a alarm message text. After that I made a run application and...
Replies
0
Views
134
Hello brothers We are contacting you because an error like [display change is currently controlled remotely] occurred while using the equipment we...
Replies
2
Views
213
Hi! I recently discovered how to get to configuration mode and disable printing for connecting to PanelBuilder32 and updating my Panelview...
Replies
1
Views
448
Last night electricians replaced the panelview and now there is no comms between the panelview and the PLC. The processor is a 1747-L541 SLC 5/04...
Replies
4
Views
900
Hi everyone, I've been tasked with creating a basic HMI for commissioning purposes for two pumps on a AB Panelview Plus 1000, 2711PRDT10C. I have...
Replies
16
Views
2,897
Back
Top Bottom