Panelview 550 not communication with 5/05

DebPeterson

Member
Join Date
Apr 2010
Location
Houlton, WI
Posts
31
Hello,
We replaced an AB 5/03 with a 5/05. We have a Panelview 550 which was communicating with the 5/03 using a DH485. The DH485 cable went to a AIC module and then to the 5/03. Tell me this please, now that we have the 5/05 on ethernet, what must I do to to get communications back between the 5/05 and panelview? The panelview is basically not functioning. I assume I need another style of module to make this possible. I am trying to recovery the panelview program using a 16K data card, but it is telling me it needs to be formatted. I think I need a 256 data card instead? We could possible install a panelview 600 since we have one on hand. Any help would be greatly appreciated.
 
What is the complete catalog number of your Panelview?

You can use the serial port on the SLC5/05 (configured for DH485) to communicate with the PV. With the above info someone can tell you the proper cables to use.
 
I think you will need to set up Ch. 0 on the 5/05 for DH-485 and use an AIC.

What model is your PV 550? and the 600?
 
It is CAT 2711-K5A2
B-Series
Revision D Firmware 1.07

see picture below for cables. And pin-outs

Configure the SLC5/05's serial port for DH485, same baud rate as your PV with a different node address.

Dh485port.jpg
 

Attachments

  • 1761-CBL-AS03 & 1761-CBL-AS09 Cable Pin-Out.pdf
    55 KB · Views: 28
  • 1747-CP3_1756-CP3-PinOut.pdf
    31.8 KB · Views: 22
Last edited:

Similar Topics

Hi. I have now a PanleView 550 (2711-B5A2, Rev A, FRN 4.20) and try to establish communication with the RS500. Tried directly between laptop and...
Replies
31
Views
5,085
Hi everyone.... we are a production company and our machine is 10-12 years old. It was running from years, the cpu is SLC 5/04 (1747-L542)...
Replies
5
Views
7,814
Hi guys..and girls if so.I'm a newbi,and also not very clued up when it comes to electronics.Can you possibily assist.My problems are:When I...
Replies
1
Views
3,711
I have a PV-550 [2711-T5A3L1] that speaks RS-485 only. If i get a 1747-PIC cable, which is a "Personal Computer Interface Converter converts...
Replies
5
Views
1,839
Hi everyone I am new at this allen bradley panelview 550 (2711-B5A8). I wrote a general flip/flop program and uploaded into the micrologix...
Replies
0
Views
4,761
Back
Top Bottom