Hi all,

I have a 2711R-T7T running an application without a shutdown button in the current program. I've looked at all the manuals and can not figure out how to access the configuration screen. Also, I can not find a way to use a keyboard except to factory reset.

I need to upload the application as we do not have a copy.

Is this possible or screwed?

EDIT: Firmware Version 5.011
 
Last edited:
Maybe there was no upload in early versions. Since I started fooling with PV800 in CCW V10 or V11 you can upload from a PanelView 800. Through Ethernet, make sure your IP settings are compatible between the terminal and the computer. Select discover and browse Linx to the terminal. You should get an option to upload the application. If there’s multiple applications in the terminal, the one running would be the one you want.

There might be an option to prevent upload, but I haven’t seen it.

PV firmware 5.011 is recent, if not current. I just uploaded from a PV800 5.011 with CCW V20 to test for this post.
 

Similar Topics

As the title says, I'm using CCW with a PV800 (and Micro850). I've made a scheduler in which a user can choose a month, day (1-31), hour (0-23)...
Replies
15
Views
514
Hello, So i managed to read the string coming from control logix and put a string display in PanelView 800. Now I am struggling to do the other...
Replies
1
Views
143
Good morning all, programming a Panelview 800, I have a maintained push button programmed on screen 1. I copied and pasted it to screen 2. Could...
Replies
2
Views
1,163
I'm trying to convert an old panelview 600 application to the 800 and I'd like to keep the current serial comms configuration instead of adding...
Replies
1
Views
601
Hi all, I had a setup with 2 Micrologix 1100 connected to a Panelview C300 over DH-485. I was mandated to upgrade the HMI, and proposed to...
Replies
5
Views
891
Back
Top Bottom