I'm trying to convert an old panelview 600 application to the 800 and I'd like to keep the current serial comms configuration instead of adding ethernet switches, etc. The processor is a 1769-L32. At some point this processor was micro or SLC and the project has been converted to 5000, so the data table addressing is now arrays.
I have the alarms banner and all integer tags working, but I cannot seem to get boolean tags that are in arrays to work. Just wondering if anyone else has attempted?
Interestingly, to get integers to work I had to change the syntax back to original 500 format, so a PLC tag in the L32 such as N7[30] becomes N7:30 in the CCW project.
For anyone that ever comes across this, I figured out that the boolean tags in the compactlogix need to be addressed as "N" file in order to work in the 800. For instance, if your project's array was converted from an SLC/rs500 project, it is probably something like: B3[xx].xx
This needs to be converted to something like N7[xx].xx within the compactlogix project. Then, in connected components address this to N7:xx/xx and make it a boolean.
Hello everyone, I hope you are well, I have a CompactLogix 5380 PLC (5069-L310ERM) and I would like to communicate with a PanelView 800 HMI...
716
Hi, I am currently working on a project which involves PanelView Plus 800 as HMI and compactlogix 1769 30ER controller. There are 400 tags that...
4,587
Dear All I hope you can help me here :) Trying to connect a Panelview 800 to a compactlogix L24ER, not as straight forward as I expected, I...
2,693
Hi experts, I have Panelview 800 Teriminal (version 4.012) connected to 5370 compactlogix L2 controller(1769-L24ER-QBFC1B). Through Ethernet...
16,425
As the title says, I'm using CCW with a PV800 (and Micro850). I've made a scheduler in which a user can choose a month, day (1-31), hour (0-23)...
510