PanelView not reading values from SLC 5/05
MartyMaucher
May 2014
Pensacola
91
PanelView Plus 400 is set to display the value from tag F8:1 which is there in the PLC and updating. However, the physical PanelView just displays "*****". The value ranges from 0-500, and the display is set to display 5 digits with 1 decimal place.
I'm not sure if the panel is communicating with the PLC.
Any ideas?
MM
PLC: SLC 5/05
Display: PanelView Plus 400
Comms: Ethernet: PLC at 172.16.100.33, PanelView at 172.16.100.32
  • UK Research.zip
As a test expand one of your numeric displays horizontally. I think that's just the 'there's more than I can fit in this space' readout. Possibly lower the font size?
Ok, I got the problem resolved - a couple things I was doing wrong:
In FactoryTalk View Studio, I had picked the tag from an old(?) Tags folder, and not from the connection to the PLC.
On PanelView Plus 400, when it prompts to replace current communication to application settings, say: Yes.​
I'm still learning the whole Allen Bradley environment.
Thanks,
MM
Hello all. I am working with a CompactLogix running version 30.12, and a Panelview Plus 700 running version 9.0. The customer wants me to read...
4,131
PanelView Plus "Timeout Reading" and "Timeout Writing" - battery low Hi all, A customer has a PanelView Plus (catalog number 2711P-K4M20D8 ser...
4,441
Quick version is is it possible to read the language that the user has selected on a Panel View? There seems to be no system flags but are there...
4,123
Good Morning, We have an application where we want to read the temperature of the a PanelView Plus 1000 HMI, and use this as a basis to determine...
1,198
I've looked at the program and don't see what the issue might be. In LAD-14 N7:60 ISO reading on HMI=3.5g/s.....Wrong should be 35 N7:61 POLY...
1,815