parameter need to siemens micro master drive

nasrin

Member
Join Date
Feb 2011
Location
madurai, tamilnadu
Posts
1
hi,
i want to work as a siemens micro master drive using two
analog input choosable, digital input 2 is disenable analog input one select, digital input 2 is enable analog input 2 select, what is the parameter need to set this functioning
 
Mm

Hi,

First of all, wich MicroMaster, an MM4 I suppose ?
If that's the case:

I think you need to configure 2 Drive Data Sets (DDS). P820 and P821. So if you enter r722.1 in P820 and r722.2 in P821, then you can change between DDS1 and 2 with the Digital Terminal inputs on input DI2 and DI3.

In DDS1 you can set that the Main Setpoint comes from Analogue Input 1 and in DDS2 you can set that the Main Setpoint comes from Analogue Input 2.

Does this help you ?

Kind regards,
Combo


hi,
i want to work as a siemens micro master drive using two
analog input choosable, digital input 2 is disenable analog input one select, digital input 2 is enable analog input 2 select, what is the parameter need to set this functioning
 

Similar Topics

Hello, first time posting. But I've been lurking on here for a while. I'm wondering what would cause parameter 12 not to change. Parameter 46 and...
Replies
3
Views
2,284
I am installing a Pro-face touch screen GP2401-TC41 with a mitsubishi QO2HCPU. The touch screen is connected with a QJ71C24N in the PLC rack. I...
Replies
2
Views
3,520
Hello all, I am currently trying to program a PowerFlex 525, version 7.0. We had a power outage recently and when the power was restored, the...
Replies
10
Views
217
Greetings, I am working on a project and I would like to scale %AI to -10.0 to 10.0 VDC. The module Input data is stored as a 16 bit Integer and...
Replies
4
Views
74
Hi All, This is my first PowerFlex 755 drive setup and I am having an issue with when I start the drive it runs at my minimum speed 5Hz, but...
Replies
10
Views
429
Back
Top Bottom