PC Communicate with NT21

sutton

Lifetime Supporting Member
Join Date
Mar 2003
Location
Singapore
Posts
74
Hi everyone,

Im now working on a project using Omron PLC CJ1M CPU21 and Touch Panel NT21.

I manage to work out the communication of PLC and Touch Panel, and the communication of PC and PLC. However I failed to set up the communication of PC to NT21 Touch Panel. Im using a RS232 cabel. I follow the instruction manual, and set up the PC comm port and baud rate accordingly.
In the Touch Panel NT21 itself, i set the memory switch Comm.B to NT link(1:1). Then i switch to Transmission mode. However the commmuncation didnt work when i try to download a screen to NT21.

Can anyone who used NT21 before tell me what step did i miss out?
Thank you.
Cheers,

sutton
 
Are both ports (PLC & screen) set to NTLink 1:1? I am more inclined to use 1:N.
 
Another thing I thought about, did you set the PT Control and PT Notify areas in the NT21. Also, the first word in the PT Control area needs to be set for a valid screen number. Screen 0 (zero) is NOT a valid screen number.
 

Similar Topics

how to communicate FactoryTalk Optix and Mitsubishi Q Series. I want to know the details of that
Replies
0
Views
56
HOW to communicate with OPTIX and Mitsubishi's Q Series PLC?? PLEASE HELP ME
Replies
0
Views
64
We are trying to poll data coming from a PLC for remote monitoring we have the IP address of the PLC and the default port number and the path is...
Replies
25
Views
608
We have some very old technology in my plant that needs adjusted but I don’t have the equipment. Can anyone tell me what I need to program this IO...
Replies
13
Views
363
Hi Guys, I want to connect my 1769-L36ERM to a different network domain, is it possible to do it using only the dual ports in the Controller? Or...
Replies
3
Views
241
Back
Top Bottom