ph soil sensor for s7-1200

xMilos

Member
Join Date
Jul 2015
Location
Skopje
Posts
6
Hi all, student project :)

I need suggestions for a pH sensor for testing the pH of soil. Using s7-1200 plc. It should be wired to the digital inputs, so i guess i need a sensor with digital output or can i use an analog one with A/D converter.

Thank you
 
You need a sensor with an analog output connected to the analog input of the S7-1200 (0-10V). The PLC already has analog inputs.
 
They are occupied, that is why it need to be connected to digital input. And i try not to use additional analog module.
 
You could look at using a Signal Board (SB) rather than a Signal Module (SM). A single input SB costs a bit less than 1/3 of an SM. It fits on the front of the PLC, you have to remove an existing cover and plug the SB in instead.

edit: of course I could have been really helpful and have given the part number: 6ES7 231-4HA30-0XB0

http://media.automation24.com/Artikelbilder/Shop800px/101663.jpg
 
Last edited:
I think you're getting a little confused about the meaning of a 'digital input' in the context of PLC's. A 'digital input' is a binary input, meaning it is either on or off. You want to measure pH, which is a numerical value. These are a completely different forms of measurement.

An A/D converter encodes a continuous voltage signal into discrete samples of finite resolution values. In fact, analog input modules should generally have an A/D converter already, as it needs to interprets the voltage level of an input signal as a 'number' for the PLC program to use in its logic. However, an A/D converter won't magically convert a numerical analog value to a binary on-or-off value.

If you want to measure soil pH, it will need to be fed into the PLC as an analog value one way or another.
 
Last edited:
First and third choices are lab sensors, so they are probably not suitable for PLC applications. Second one employs a Modbus RS485 interface, which is usable with a PLC. However, I don't think S7 supports the Modbus protocol natively, so you may have to acquire a communications module.

If you want to read pH into a PLC input, you need a pH transmitter that can output either a 4-20mA signal or a 0-5V signal, as those standard signal ranges are what PLC's generally use.

EDIT: Something like this: http://www.omega.com/pptst/PHTX014.html
 
Last edited:
Thanks again you were very helpful.

I decided to go with Sensorex PHMA pH Transmitter (2-Wire, Blind, Non-Isolated) + S8000 Modular pH sensor platform and additional analog module for the PLC.
 

Similar Topics

I just got a interesting request. I have a customer that is wanting to detect how much moisture there is in the soil around a Pipeline. I have...
Replies
2
Views
2,017
hello, i have a problem in wiring my relay module board 5v from plc to my soil moisture sensor, i already have a 5v power supply, i just dont know...
Replies
6
Views
5,240
We have a raised hopper at our plant that gets filled with soil. Our problem is that we can't see the hopper to see when its full as it is in a...
Replies
27
Views
9,281
Dear, i was wondering if somebody came accross a code or standard such as from NFPA that requires the use of Flame Detectors for Gasoline, Gasoil...
Replies
6
Views
4,618
Hello, all. I have currently been tasked with automating the irrigation system at a vineyard for table grapes. The work with turning the water on...
Replies
5
Views
1,781
Back
Top Bottom