Pid Cascade Loops Rslogix 5000
learner
Apr 2007
British Columbia
81
Hi there,
I need to wite the logic to control a cascaded PID loop with the following characteristica:
1- Master : Density
2- Slave : Water Flow
the customer requires that this loop has the following modes:
1- Master (Auto / Man / Cascade)
2- Slave ( Auto / Man / Cascade)
According to Rslogix 5000 Help menu, When you connect the two loops in cascade foramt, and in configuration tab choose the master and slave, and put them in automatic mode the two loops work in cascade mode.
However my client requires that that the loops, espacially the slave must have the "AUTO MODE" ,with independant set point, so he can tune the flow loop independantly ,using the flow transmitter.
My questions are:
1- is there a good reference regarding cascading loops in RSLOGIX 5000 to refer to.
2- When a loop is configured as SLAVE, Wouldn't "Auto mode" put it into Cascade mode automatically. basically, I would like to know if a loops is configured as a Slave cascade loop, how can it have independant Auto mode with separate set point.
Regards
Why not set up the loops as Cascade the old way; 2 seperate
loops. Then provide the option of moving the output of loop
1 to loop 2.
This is how we do things which is not to say you can't do this
with the Cascade feature of CLX.
Good Luck,
(8{)} :) .)
(Yosi)
Learner,
I just went through a similar process and posted the same question here. The consensus was that the Master/Slave setup in Logix5000 is too constraining for doing what you describe. As the second poster said, do it the old fashion way. That's what I did. Treat them as seperate loops with the output of the outer loop going to the setpoint of the inner. When you want to run in inner only, use a different manual setpoint for the inner loop. When you want to run pure manual, put the loops in SWM mode.
Hi Folks I am beginner at plc programming and I have got some questions about PID cascade. I look for some programs( I work on Step 7, Tia...
1,353
Hi, I am trying to automatically regulate a process ( liquid ) in a tube using an ultrasonic sensor, differential level meter, control valve...
3,169
Hey guys, After spending most of a day Googling looking for the answer, I finally decided to make a thread and ask the experts. I'm trying to...
3,608
Hello!! I'm working on a project that requires a Cascaded PID Loop to control solution temperature in a tank with a water jacket. The tank has...
2,413
RS5000 vs.20, 1769-L35E Processor, I have had an issue that I have seemed to work out between all of the PID posts I could find here and listening...
5,400