You may be fighting the wrong problem.
Most level control system should be easy. If it isn't there is usually a design problem and no matter how the control guy tunes the system it will not put out more than 100%. It is time to start asking the system designers.
Reduce the error to 0. So why can't the error be reduced to 0? If it is because the outflow is more than what the pump can supply then there is nothing you can do!!! The pump will run at 100% just trying to keep up let alone reduce the error. Are you sure the pump is running at 100% when you give it a 100% signal? If so then you got a pump sizing problem.OK lets forget about 2 PID loops
Let's say I have one level control SP 80 PV 70 OUT 100
How do I prevent the integrator from windup?
Most level control system should be easy. If it isn't there is usually a design problem and no matter how the control guy tunes the system it will not put out more than 100%. It is time to start asking the system designers.