PID output scaling PLC5
russrmartin
Aug 2002
Eastman, Wisconsin
744
Hello again. I have a question about PID controls. When looking on at a PID control block in a PLC 5, I can see where the input range is scaled from engineering units to the 0-4095 value that the PID block uses. However, I cannot see where the output value is scaled at? Is 4095 a constant in AB PID control variable words, or is there somewhere that one can designate 0-4095, or 32767 to -32767, etc. I'm just trying to get a little better grasp on this. Also, is there anywhere a guy can get a cheat sheet for the abbreviated bits in a PID data table. I don't know know what a DVNA, or a OLH bit stands for. I cannot seem to find a description of what each one is and what it's full name is. Any explanation on this subject is welcome. Thanks.
Russ
New info
Since posting my last thread, I have read in an analog input card manual that the digital resolution is 1 part in 4096 bits. It also shows that the output range is 0 to 4095. This answers most of my question. I didn't think to look at the modules manual. Thanks anyways.
Russ
have you looked here?
the information on the parameter names that you're asking for can be found in:
the PLC-5 Instruction Set Reference Manual
you really need to study all of chapter 14 (PID control) ...
the parameter names you're looking for start on page 14-18 [Adobe Reader page 206 of 372] ...
and to answer your specific question: the PID instruction for the PLC-5 always gives an output which ranges from 0 to 4095 ...
Hi, I've got a PID block in my RX3i program wherein the setpoint is 390, my feedback is 200, and the CV is the difference, 190. When I change PV...
1,288
I've been chasing my tail for a couple of hours now, trying to get the output of the PID instruction to generate a value of 4095 for 100% output...
2,310
Hello, I have a motor that we are sending a RPM Speed Output from 0-100% to the VFD. However, the Motor HP needs to be limited to 6000 HP and the...
92
Hello Friends, I am looking for a way to take my PID Output( it is the result of my PI Algorithm in Real format) and generate a PWM Signal in...
2,525
Hello, I have a flow control PID that keeps locking up. It seems to control fine but after a while the output no longer moves. For instance...
970