PID Problem
ibrahimanwar
Dec 2016
cairo
i want to ask if it possible to make PID temperature controller with one valve single acting and how to do that
as :
i have a problem with my system i suppose to make PID Temperature controller
the input is the Temp (Ai ------> 4-20 ma)
but the output is a valve with single acting (just one digital output)
this valve is to control the hot water that increase the temp
i can not use FB59 as i have only one Digital output all the time taking action even when
Process value = Set point ------> stopping the open command means closing action
i hope someone can help
If you have a long lag time in your process you can open your valve for say 16 seconds and close it for 4 seconds, then repeat, for an output of 80%.
Do some valve life calculations and lag time measurements to work out how large you want to set your duty cycle. (20seconds in the above example).
As Bitbucket said. You can use "time proportional" control with the PID CV output. Just be sure that you operate the solenoid for at least the minimum specified time it needs to avoid problems.
If you tell us what PLC hardware you are working with, we can point to code examples.
You may also want to try Sliding Mode Control (SMC) as mentioned in this thread, among others. You can use the search tools to find other threads, but this one was most helpful to me a while back.
What is the temperature tolerances. You may be better off with a simple on-off control
with a deadband. No PID necessary , use compare instructions.
Dear all . I made a program for boiler tank using TIA V15 , the program consists of 2 PID blocks in OB30 . but the PID didn’t work automatically...
2,672
Dear all . I made a program for boiler tank using TIA V15 , the program consists of 2 PID blocks in OB30 . but the PID didn’t work...
1,134
Hello Friends; I am working on a GE Funac LM 90-30 software. I face the problem to set the CV value when PID in auto mode. The parameters are set...
3,052
I had a problem on a hydraulic servo controlled cylinder, which I believe was caused by the PID loop and the cylinder reaching a hard stop at one...
2,460
We have a machine we're trying to commission. It's a web converting machine. It takes webs of foil, wicking paper & a label and creates a chemical...
1,312