Started receiving this error on some of the C-More HMIs that are part of the plant network. There does not seem to be any issues with functionality.
No PLC programs were changed.
Only three of about 32 PLCs on the Ethernet network are creating the errors. Once is a Micrologix 1100 and the other two are SLC 5/05. They are connected to the HMIs via an unmanaged switch, which was changed
Rebooting the entire network didn't help.
I went through all of the PLC programs to ensure there were no tags that referenced addresses not present in the PLC programs and didn't find any
All devices can be pinged fine, with no time-outs
Any suggestions?
Press the upper left corner of the Cmore for ten seconds, say Yes you want the System Screen and go to the Information button. Once in the Information section, go to the error tab and it should give you a bit more information.
(Stolen from Automation Direct Customer Service)
Actually, it seems the issue is related to ping timeout. I just didn't let the ping tests run long enough.
Haven't had much time to troubleshoot today, except for moving the cables from the affected PLCs to different ports on the switch, which made no difference.
Solved!
The problem ended up being a fiber cable connecting two switches. I didn't replace the cable - I just replaced it with an ethernet cable and the problem went away
Hello, I want to connect the Factorytalkview ME with rslogix500 to see the live response of HMI buttons in Rslogix500 ladder code . I am using PLC...
38
I have a cell with a compact guardlogix as the plc and I have three hmi's and two vfd's on this cell. I been experiencing momentary comms faults...
86
Hi, hope you doing well I am looking for SIEMENS PLCSIM equivalent in GE FANUC PLC, RX3i PLC thank you
30
Hai, I'm working on Allen Bradely PLC RS Logix 5000 V20 i tried to communicate modbus communication with AB plc and RS 232 to Ethernet converter...
55
Trying to learn PLCs going to start by buying an Arduino Opta Wifi to practice with but what's the PLC I should get next?
255