PLC 5/60 Block Transfer Issues

astrange54311

Member
Join Date
Dec 2012
Location
Wisconsin
Posts
2
I am having issues at a plant with the BTR and BTW instructions giving me an error code of -10 or -11 even though the chassis data is correct. I ended up having to wipe the PLC 5/60 and reload a known good program because the other BTW and BTR were stuck on enable and would not error out. There was a large snowstorm that may have caused some power issues, but I haven't been able to nail down this error.
 
I think we would have to see a snap shot of the program when the error(s) occurs.

Here is what the manual says about the errors.

BlockTransferError.jpg
 
The rack itself is working and the digital I/O is working properly, it just seems that the analog cards NI4 NO4I will not accept BTW and BTR. Is there a way to reset the analog cards via the direct IO addresses? Example this is rack 6 and in it is the ASB, then an IA16, NI4, NO4I so the I:6xx or O:6xx.
 
I have never used a PLC5 to a remote I/O with SLC I/O cards before.

Some put a parallel branch in the BTW rung to toggle it, to configure the card manually.
 

Similar Topics

Good Evening , I need to convert a PLC 2/17 ( RS Logix 5 ) over to a CompactLogix 1769-L33ER . I took notice in the RS Logix 5 program that...
Replies
9
Views
2,094
I really need to wrap my head around a PLC-5 , Block Transfer Write. I am dealing with some alarm issues with a PLC 5 and Panelview Plus. I want...
Replies
1
Views
4,791
We removed an HMI talking on the RIO only to find problems with the remaining devices on the RIO network. The network sped up significantly only...
Replies
4
Views
1,761
hi,i have a PLC5 system with something wrong.the cpu was plc-5/80e.with 14 chassis 1771-A3B.the first 13 chassis each has 10 1771-IL 8 analog...
Replies
2
Views
3,613
Please tell me the how to get out of this error Problem is the BTW enable bit is continuously on and block transfer is not executing. Is...
Replies
2
Views
1,745
Back
Top Bottom