No more block Transfer exit S:10/7 PLC-5
nirmitpanchal
May 2011
mumbai
Please tell me the how to get out of this error
Problem is the BTW enable bit is continuously on and block transfer is not executing.
Is there any problem in BTW?
See PDF below (first page last paragraph).
It would also help if you could post your .RSP file ( zip it first then post).
Attached for your reference
Panel view standard terminal has been communicated as RIO.
Its Rack no assigned 10
and all the tags are based on RIO configuration.
Online program doesn't show fault (for Rack 10) in channel 1B(remote I/O scanner) properties.
Communication LED of processor and Panel view standard terminal is ok(green)