I'm a bit confused by your question.
The example shows the MSG instruction residing in PLC5 and doing a READ FROM Contrologix to PLC5. On successfual completion of the instruction the data from the contrologix will be in N7:0... of the PLC5.
If, instead of doing a READ, you do a WRITE from PLC5. Then whatever data you have in N7:0 in PLC5 will show up in technote_data in contrologix.
to change from a READ to WRITE, change the Communication Command from PLC-5 Type Read to PLC-5 Type Write.
I followed the instruction @ this site:
http://plcview.blogspot.com/2012/02/...hernet-to.html
If I were to write to the "technote_data" array in the controllogix PLC, would that data show up in the PLC-5 or is the instruction only for data flowing from PLC-5 to the controllogix
If your ControlLogix program puts a value of "1234" in technote_array[0], that same value will appear in N7:0 on the PLC-5.
The MSG instruction in the example is for reading data from the ControlLogix to the PLC-5.
If you were to write data from the PLC5 to the "technote_data" array in the controllogix PLC, then that data must exist in the PLC5.
Perhaps you could explain precisely what data you want messaging, from where, to where, then you will be guided how to do it.
Hi Everyone, I am currently trying to communicate ControlLogix PLCs via EtherNet/IP with Delta V DCS. There is a VIM2 card configured for...
299
This is for more of a personal project, but I am wondering if anyone has done communication between the Automation Direct Click PLC and a...
2,512
Hi, I am trying to make connection between PLC 5 processor to DH+ module in contollogix chasiss directly. Is that possible? Thanks,
2,540
I'm working on a project where there are three generators that are used to bring power to a facility in case of emergencies. There operation is...
4,799
Hello, I want to establish the communication between Controllogix plc (2756-L62) to wireless Barcode scanner (MT2090) through prosoft...
5,850