PLC faulting intermittently Fault code16
Jai_mrf
Mar 2016
Trichy
I am facing problem of my Plc going to fault mode intermittently.
on my AB Compactlogix PLC
Fault coming is
code16#009 module configuration rejected, parameter error
Additional fault code 16#0300
This came on 1769IF4 module
When restarted PLC it is running OK
This is the last fault coming
Before this another fault code had come before in the controller
"IO module connection failed on required"
Till now i have changed 1 IF$ module, One end connector, changed the power of IF4 drom bus to external
Kindly help
Jayakrishnan
By end connector I assume that you mean the 1769-ECR (end cap)? I just wanted to be sure because this part is necessary with CompactLogix, some people don't realize this.
Every time I have experienced something similar to this its because the white tabs on top of each module that lock them together weren't fully seated (to the left). They would appear to be all the way, but if you pushed on them, you'd feel the "click" of them fully seating.
If that is not it, could you describe the entire rack part numbers? Include the power supply and where it is in the rack. For example:
[0] 1769-L33ER
[1] 1769-IQ32
[2] 1769-IQ32
1769-PB4
[3] 1769-IF4
and so on
Need some assistance. I am testing out a heart beat code and I want to fault the processor so I can check from the SCADA system that the PLC is...
29
6,977
So when going through creating logs of all our safety signatures for tracking purposes. I found one PLC without a safety signature. This one is...
9,065
Hello- I have a Controllogix PLC with 2 remote I/O racks on Ethernet I/P. It has been going into fault after a few power outages they've had, and...
1,512
Hello, Attached is my PID setup. I am trying to vary the speed of a pump to keep water in a tank at 70 inches. Everything works, as long as my...
3,058
I have a PLC 5/30 in a 1771-A1B that are running in part of our plant. Everytime we have a power blip, the processor will fault. The processor...
3,609