Hi. My background is 35+ years in field instrumentation and I'm doing a college PLC project for a mixing & batch system with pumps, high/low tank level switches, agitators on timers and open/close type valves.
I'm trying to design the ladder logic diagram. With regard to the level switches, do I have them operate their own (internal ?) plc relays ? Should I use n.o. contacts on the level switches in order to operate their respective relays when reaching the high or low levels ? I read somewhere that this way gives a positive 'on' or logic '1' but it contradicts switch wiring used for high/low alarm purposes i.e. 'failsafe'.
Apologies for what looks simple enough but, I need to ask as I am a little confused.
Any other tips to include in the ladder logic would also be greatly appreciated. (Advice on agitator timer setup/wiring etc)
Thanks.
I'm trying to design the ladder logic diagram. With regard to the level switches, do I have them operate their own (internal ?) plc relays ? Should I use n.o. contacts on the level switches in order to operate their respective relays when reaching the high or low levels ? I read somewhere that this way gives a positive 'on' or logic '1' but it contradicts switch wiring used for high/low alarm purposes i.e. 'failsafe'.
Apologies for what looks simple enough but, I need to ask as I am a little confused.
Any other tips to include in the ladder logic would also be greatly appreciated. (Advice on agitator timer setup/wiring etc)
Thanks.