PLC losing parameters
Bradford0662
Jul 2022
Georgia
Good Morning All,
I have a Siemens 6ES5 466 PLC. We are intermittently losing parameters . We can pull the backup battery and power down. When it restarts, it loads from eeprom and runs fine for a while then all the parameters go to 0. Any help would be much appreciated.
6ES5 466 is an analog input card in an S5-115U rack, or an S5-135U rack or an S5-155U rack.
Suspects:
Electrical noise.
Brown-outs.
Defective CPU.
Defective rack.
Defective rack power supply.
Maybe combined with battery is low.
No matter if the PLC is an S5-115U, or an S5-135U or an S5-155U, it is totally obsolete, spare parts are difficult to get and are expensive.
A modern PLC will also have better diagnostics so you might get useful information to narrow down the error.
So........... time to bite the bullet.
So you can write your way around this most likely until you can catch and nail the problem down.
use a Equal block, if the operational value is equal to zero(if its not supposed to be) then then a move block to mov a fixed value to that operational value.
Of course this can also lead to complacency and you forgot about it,, then boom.
I am working with beckhoff plc in twincat 3 environment. I have a array of struct which I want to make persistent. I declared it with...
113
Have a PLC5/40E that has a battery installed and a working battery warning light that is off with the battery plugged in. There is no memory...
2,734
I am using a LS PLC - DR60SU - to control various control loops. I have set up the PID loops in the PLC and am using an HMI to set the sepoints...
3,442
Hoping to catch a seasoned guru's attention on this thread who knows these drives. We have 3 PowerFlex 700s controlling fan motors in a cooling...
28
9,771
We had a power glitch last night at the factory. 15 minutes later when the power came back, all the PLCs came back to life except for one PLC...
3,293