For those who don't have RSLogix 5 handy, here are the RIO scanlists for Channels 1B and 2A of his PLC-5/60 controller.
Another concern I would have with this system is that there are 25 BTR and 25 BTW instructions (just a quick count) and that implies at least 25 analog modules.
The ControlLogix has a limitation on how many MSG instructions it can "cache", which how most analog module messaging is done. I have to look up what the limits are now, but I recall 16 on DH+ and 16 on RIO being the limit. It's possible they are combined now.
My rule of thumb is that any PLC-5 system with more than 16 analog modules is a good candidate for the 1756-RIO module because the Block Transfers are handled by the module, not by the ControlLogix itself.