PLC's and NFPA70E

cornbread

Lifetime Supporting Member
Join Date
Feb 2007
Location
madison, indiana
Posts
407
A bit off topic... Wondering how other factories handle NFPA70E and accessing PLC's. In most plants I've worked in we have the PLC and 480V disconnect all in the same cabinet. Now with 70E "working on are near live equipement" they are asking me to suit up as if I was going to work on the 480V. I know where they are comming from..never can tell when an Arc Flash or accidental contact. I've tried to use 70E as justification to get my PLC networked. Interested in how other folks handle this situation.
 
For existing equipment either external programming ports or network the PLCs has been the approach by most that I have seen. For new equipment I like to use a power distribution cabinet separate from the PLC cabinet which only contains 24VDC, plus the external prog port.

We also have a lot of clients requesting us to perform Arc Flash Hazard analisys for there facilities. This way you can determine what your arc flash boundaries are for all buses, panels, mccs, etc. and what PPE is required to work inside them with power on. That last 3 months I've been doing Arc Flash studies and calculations like crazy.
 
Last edited:
I have had several customers order cables (custom lenght) they would leave the cable plug into the PLC and have the 232 side on the outside of the cabinet, then they don't need to open the door
 

Similar Topics

Hi looking to install a smaller less sophisticated PLC for fountain timing and also one analog pressure sensor which would be used to detect...
Replies
0
Views
1
Hello all. I recently had to re install my AutoCAD Electrical 2024. I am trying to find the Rockwell catalog to install in it but cant find...
Replies
0
Views
60
Hello, I have an issue where I want to simulate an Siemens HMI panel, through NAT connection to a PLC. I have the possibility through extended...
Replies
1
Views
41
I had a call yesterday that a light had come on, on the panel saying 'battery low' and what it meant and which battery? This was from a program I...
Replies
4
Views
137
Hello, im quite new and still learning. I would like to ask is it possible for FATEK PLC to read data value more than 16k? I'm trying to move my...
Replies
0
Views
69
Back
Top Bottom