Pneumatic control valve
Abdul03
Jun 2012
England
77
Dear Friends,
I have a project in which I am working on an existing chiller plant, It's complete pneumatic and a very old system. I have a control valve which is controlled by 3511 pneumatic rotary positioner.
It consists of supply air, input air (from instrument) and valve output. I applied supply air of 20 PSI and given a input signal of 3-15 psi using a pneumatic pump. I just don't knwo how to operate this valve. I am working on pneumatic controls for the first time. I appreciate if someone could able to help me to find a solution to this.
I hope there could someone who has good knowledge on pneumatic controls.
Thank you,
You probably have an I/P converter to control the valve.
If you send 4mA to the I/P, the I/P sends 3psi to the valve and the valve stays closed and if you send a 20mA signal, the I/P sends 15psi to the valve and the valve opens completely. the signal can also be inverted cool/heat but this is the idea.
the supply should be around 60 psi, as there is a strong spring in the valve.
on the valve stem is a lever going into the positioner.
i have seen a lot of wear on the o rings of the very small cylinder giving air to the ports.
internal is a flapper nozzle system to the lever.
i took out all positioners and put the instrument line on the valve direct.
outside the coldroom i took out all I/P converters and replaced them with 5/3 valve now i can give it a pulse to open or close the valve.
inside the room is only the valve.
take care to dry the air.
You are correct Mickey. I guess I didn't pay attention to the post "3511 pneumatic rotary positioner".
Hello experts, There is a control loop with PID controller and pneumatic actuator that controls the position of the valve. Pneumatic actuator has...
2,247
Hello, i would like to control a pneumatic valve based on conductivity of the medium in the pipe. I want to receive OPEN and CLOSE feedback as...
1,392
Hi Gents, Please could someone assist me in understanding this piece of equipment as to how it works. Any feedback would be greatly appreciated...
3,919
Hello guys, I'm in a bit of a dilemma - not very clear on the operation the typical PID controller. Here's the issue: A client has a turbine...
3,791
I don,t know how to design a ladder to control operation of pneumatic valve with PID input?
2,960