PNOZmulti to Panel View Plus

schui

Member
Join Date
Sep 2011
Location
Toronto
Posts
51
Hi All

I have connected a PNOZmulti to an Allen Bradley HMI (PVP 1000) using OPC Kepserver.
I am having some problems in getting the data from the multi controller, I have the data booklet from Pilz defining the different bytes needed for the data, such as the Run, Diag, Fault, IFault and OFault. Problem is when I define the tag in the OPC as a Byte it rejects it as invalid. Has anyone any ideas?

Another problem is I don't know how to setup the alarm messaging in the PV I am able to get the required Tags in the OPC but I cant get them to trigger as a message, if anyone can give me some guidance I would much appreciate it.

Thank you

Capture.jpg
 
Looks like the register returns two bytes. Have you tried using a 16bit(word) tag in Kepware? I bet you could try calling Kepware tech support, if you haven't tried Rockwell.

To create alarms out of the Kepware tags, add Kepware as an OPC server to your FTView ME project. Then you can browse those tags from the alarm setup in FTView Studio.
 
Hi Schui

I believe you are in the wrong Data area for the diagnostic lamps on the base until for the multi, I had this same issue only recently.

If you go to pdf page 94 of the PNOZmulti interface manual, there you will find the mapping, be careful though as I found out that there is a shift of one bit.

.0 is not used
.1 - OFault
.2 - IFault etc...

Gotta love Pilz.........

Screen Shot 2015-05-27 at 6.59.23 PM.jpg
 

Similar Topics

I HAVE B&R POWEL PANEL 400 HMI. THE ISSUE IS HMI NOT BOOTING, DISPLY SHOWING CONTIUESLY (ATTEMPTING TO A BOOT HARD DRIVE....)
Replies
1
Views
60
Is there anyone who can help me regarding this HMI is missing the choices when I make a new Device in TIA. Only 7" Display above are the choices...
Replies
3
Views
108
I have a German programed ME program. I want to know what tag in the PLC a latched button turns on. However when I open up the tag properties I...
Replies
14
Views
230
We are considering dropping our UL membership because most of our customers do not care if we are a 508A shop. However, there may be times when a...
Replies
8
Views
424
Hello, I need to create an automatic transfer panel that connects to the generator when the mains power is cut. I can draw up to 60kW and draw up...
Replies
0
Views
102
Back
Top Bottom