Point I/O Configuration problems?

bobwithdana

Member
Join Date
Dec 2003
Location
california
Posts
239
I just configured a 1734-AENT module on the tree of a Logix 5000 program sucesuffuly. I then added the 1734-IE2C 2 Channel analog input module and I cannot download it to the PLC. I get 2 errors.

Error: Attribute list error.
Error: Failed to download modules.

Then when I try to look at the analog module offline I get another error

Failed to create module profile. Module profile not installed.

Any Ideas?
 
Two suggestions:

If you are using v13.00 of software, could be necessary to upgrade to 13.04. It is a known issue with point I/O profiles.

Another idea is to save your program to L5k format and then reopen it (ACD file corruption)

Least but not last, try to install newer I/O profile from this link:

Link AOP

Hope this helps... 🤞🏻

- [font=comic sans ms,sans-serif]fuzzy logic[/font]
 
Two suggestions:

If you are using v13.00 of software, could be necessary to upgrade to 13.04. It is a known issue with point I/O profiles.

Another idea is to save your program to L5k format and then reopen it (ACD file corruption)

Least but not last, try to install newer I/O profile from this link:

Link AOP

Hope this helps... 🤞🏻

- [font=comic sans ms,sans-serif]fuzzy logic[/font]
yea,i totally agree with you ,i have some experience with the same puzzle,then i update software ,and the problem is solved !
 

Similar Topics

I'm trying to configure a Spectrum 1762sc-OF8 module connected to MicroLogix 1400 for 4-20mA, needed help. Following the user manual's sample...
Replies
0
Views
1,130
Does anyone know why Rockwell defaults the Point I/O analog modules to 16383 (Hi) and 3277 (Low) for the analog scaling in the card configuration...
Replies
7
Views
5,628
Before anyone asks, I don't have access to an AB processor... The documentation from AB suggests that the only way to configure Point IO with a...
Replies
11
Views
4,679
Hi Guys I have few questions regarding a setup of a RTD input module 1734-IR2, the module is in a Point I/O rack with a Ethernet Adapter...
Replies
1
Views
6,221
Hi, I have configured point IO module 1734-OW4(4 Point AC-DC Relay Output)with compact logix PLC. When I try to alias a tag with the one of...
Replies
1
Views
4,273
Back
Top Bottom