Power flex drive 525 control error during direction test

Chauhanraj

Member
Join Date
Feb 2024
Location
Pune
Posts
2
I am trying motor startup with pf525 drive by using wizard start over ethernet communication but during direction test it's showing control error and motor is not starting.
 

Attachments

  • 20240222_210046.jpg
    20240222_210046.jpg
    225.3 KB · Views: 10
You need to inhibit the module in your IO tree. You can't have the processor as owner while using the commissioning wizard.
 
Thanks for your support.I have tried with CCW software,this time start button option is showing in direction test wizard.I am pressing start button but motor not moving.
I have a doubt on safe torque terminal s1,s2 and s+ . Should I put jumper on these 3 terminal to run motor?
 
Thanks for your support.I have tried with CCW software,this time start button option is showing in direction test wizard.I am pressing start button but motor not moving.
I have a doubt on safe torque terminal s1,s2 and s+ . Should I put jumper on these 3 terminal to run motor?

Yes...it comes factory with a red jumper on those three terminals. If the Drive/HIM says Not Enabled then that's the issue. It will say Stopped when the STO is satisfied.
 

Similar Topics

Hi I want to set IP 172.16.27.90 in AB Power Flex 755 drive. I do set the IP by parameters 38-41 with other settings (subnet, gateway) but...
Replies
7
Views
2,471
I'm looking at how to configure a (new to me) Power Flex 753 drive. The part number is as follows and has been specified by a third party...
Replies
6
Views
2,363
i have a problem in the drive 30 kw used with motor 4 pole (1770 rpm ) , and the motor used to run load with pulley ratio 2.3 so the load speed...
Replies
11
Views
4,902
F005 fault appearing on power flex drive plz tell me how to reset
Replies
8
Views
2,364
Dear friends i have to control the speed of 3KW power motor In forward and reverse direction through PLC. PLEASE tell me the all the parameter of...
Replies
4
Views
2,369
Back
Top Bottom