Power flex drive
F005 is an over voltage fault. Simply pressing the stop button on the front of the drive will reset it.
There are other ways to reset your drive depending on the part number and how it is connected to your PLC.
Pressing the stop button on the drive didn't reset the fault?
I'm certain that will reset the fault. If your problem is something else, I would encourage you to provide as much detail as you can.
If you are looking for advice as to why you are getting a F005 fault, it is typically because something is driving your motor. For example, a heavy load trying to stop too fast.
Describe all of the hardware involved, the specific application and what you are trying to solve.
Or, there really is a line over voltage condition and it is still there after you reset it...
Most likely cause of that is fault is regen being dumped on the dc bus of the drive from the motor. Adjust your decel and or ramps and run again. If you can’t you need a braking resistor.
One thing I see sometimes is when a drive is set to "coast" stop mode and is stopped and restarted again quickly before the motor stops, the drive will try to start from 0Hz and the resulting regen causes the overvoltage trip.
I agree with jraef. What voltage are you reading at the incoming power terminals of the drive? Resetting the fault is one thing, but knowing what caused the fault will help minimize any future resets.
I am trying motor startup with pf525 drive by using wizard start over ethernet communication but during direction test it's showing control error...
191
Hi I want to set IP 172.16.27.90 in AB Power Flex 755 drive. I do set the IP by parameters 38-41 with other settings (subnet, gateway) but...
2,474
I'm looking at how to configure a (new to me) Power Flex 753 drive. The part number is as follows and has been specified by a third party...
2,364
i have a problem in the drive 30 kw used with motor 4 pole (1770 rpm ) , and the motor used to run load with pulley ratio 2.3 so the load speed...
4,905
Dear friends i have to control the speed of 3KW power motor In forward and reverse direction through PLC. PLEASE tell me the all the parameter of...
2,373