Power loss messing up Profibus network
orense
Apr 2006
Norway
196
Hello,
I have a Siemens 315 -2PN/DP plc, that is connected to a WAGO Profibus slave module, and a MP277 touch panel, through Profibus.
The WAGO module is placed inside a fan module that is supplied with 400 volt. That is where the module gets it power from, through transformers.
The plc is in the middle of the panel and the WAGO slave on the topology.
When we turn of the power on the fan module, and the slave looses it's supply, all the numbers on the panel becomes ###, hence something happens to the Profibus between the cpu and the panel.
If we only remove the Profibus plug from the slave module, then nothing happens to the panel.
Can the cpu distinguish between the slave disappering because of power loss, or because of plug removal?? Sounds strange to me....
Anybody have any suggestions to why there are differences in the two scenarios where the slave goes down?
brg
Andreas
Hi folks ! Got an older Modicom BM85 and I suspect that it's not passing data to ModBus+ network. We had a power loss for a few days and I suspect...
70
Hi all I am working on a retrofit project. There is one backup pump with Powerflex 753 drive controlled by 2 different PLCs(one 1756-L63 ,one...
1,536
Whenever we lose power to the the machine, the PLC loses its program. But as you can see in the picture, the battery fault LED is not ON. Also...
4,737
Hello, PLC rookie here working with an AB CompactLogix LI6ER in RSlogix 5000. So far I've only used structured text. I'm working on an...
2,758
We had a problem that I have never seen before. 1756-IF8I card with channels 1-4 powering field devices. This card has been working for several...
1,637