Dear All,

Please help me: to connect Allen Bradley Power Monitor 1000 - with RSLogix 5000 - 1769-L32 E processor on Ethernet. I think I have to add the device as generaic module configuration but I am not sure what will be the data format and values of input and outputs. Kindly help me on this.

Thanks


🔨
 
You can use the Generic Ethernet Module object to connect to the PowerMonitor 1000's User-Configured Table. There's a good description with screenshots in the PowerMonitor 1000 User Manual in Chapter 5, starting on page 40.

All the other data tables need to be accessed with MSG instructions or by RSEnergyMetrix software.

The Quick Start and the User Manual for this device are very good:

http://literature.rockwellautomation.com/idc/groups/literature/documents/qs/cc-qs017_-en-p.pdf

http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1408-um001_-en-p.pdf
 

Similar Topics

Hi. I’m looking to replace a basic Shark power monitor with a newer one with communication options, probably PowerMonitor 5000. The existing one...
Replies
2
Views
998
Can anybody help out with this...somebody has sent me the ZIP for the PowerMonitor_AOI_FP_1.1 and asked me to import it into a PLC program I'm...
Replies
4
Views
1,147
I'm looking for recommendations on 3-phase power monitors with Modbus TCP protocol. I've been using a Socomec Diris A10 to monitor 3-phase...
Replies
14
Views
4,317
At my wits end.....I have a Siemens S7-1200 and a Sentron PAC3220 Power Monitor. Got the MB_Client command to connect and work in TIA 15.1 but I...
Replies
3
Views
1,621
good morning all I have several red lion da30d using crimson 3.0 on the controls network in the plant. I am thinking about getting the AB power...
Replies
3
Views
2,168
Back
Top Bottom