I have a PowerFlex 70 that I have digital inputs one and two configured for Start and Stop-CF respectively.
When I have bring the Start input high and the stop low, there is a stop asserted from the digital inputs on the VFD. When I bring the start input low and the stop input high the stop asserted goes away and the drive is shown as stopped but ready.
I am already controlling the VFD through a 20-Comm-E so I know it works.
Why is my start input causing a stop to be asserted at the VFD?
The default configuration of the Digital Inputs on a PowerFlex 70 is:
Input 1 = Stop/Clear Faults
Input 2 = Start
The "Stop/Clear Faults" function on the discrete input terminal functions as reverse logic. When the input is low, the discrete input asserts a Stop command.
See the example on page 1-13 of the PowerFlex 70 User Manual for the default "3-wire" start/stop wiring circuit.
I have to remind myself of this when I am also using a network interface, because the network interface asserts a stop when the Stop bit is 1.
Ah ha!
Thanks a ton. I'm so use to networking drives that I never bothered to notice the reverse logic on the stop command.
You rock.
Hello everybody, I am connecting my DCS digital output (115VAC) to AB PowerFlex 753 Digital Input. We are using the 20-750-2262D-2R I/O option...
4,898
Hello, Currently I am controlling the Powerflex 700H via Ethernet and everything is working well. The client is wanting Auto/Manual function...
1,871
Good Morning , I am trying to setup a PowerFlex 755 and I can't get my head wrapped around the digital I/O setup concept. It doesn't look...
3,878
Just FYI, Powerflex 70 Digital Out 1 terminals are 11, 12, 13 (11-Not fault, 12-common, 13-fault). And Digital Out 2 terminals defaults are 24...
4,284
I Posted through this Thread... http://www.plctalk.net/qanda/showthread.php?t=70318
2,376