PowerFlex 70 Monitor DigIn Values Over Network?
jrsnydley
Dec 2014
Minnesota
155
Hello everyone, I have a PowerFlex 70 that is controlled by a 1756-L73 controller via a 1756-DNB and 20-COMM-D module. DigIn 1 Sel (parameter 361) is set to "1 - Enable" The 24VDC comes from the drive, through a pull cord, and back up to terminal 1 on the drive. I would like to monitor the value of DigIn 1. I am wondering if there is a way to do this over the network or if I would have to wire it up separately to a 1756-IB16I.
This should be relatively easy.
On the PowerFlex 70, Parameter 216 is the raw values of the Digital Inputs.
You can add that to a DataLink, which will require a re-configuration of the I/O connection and re-mapping in the 1756-DNB scanlist.
Or, you can send Explicit Messages to the Parameter object in ladder logic.
This would be a "Parameter Read", which is Service 0x0E hex (Get Attribute Single), Class 0x0F hex(Parameter), Instance 216 decimal (Digital Inputs), Attribute 0x01 (Value). The MSG block will gray out everything but the Instance field when you select "Parameter Read" as the service.
Is there a way to pull the heatsink temp from parameters to the PLC? I've had a couple critical drives fault recently for failed heatsink fans. We...
2,151
I've got a Powerflex 700 that doesn't like to get going in the mornings. This motor will run anywhere from 30 seconds to 5 minutes before it just...
173
So I have a sort of unique situation where I'm wanting to run a PF755 from the IO and over ethernet. Of course, this comes with it's own set of...
276
Hi I was wondering I need to update the firmware of a 755 inverter does the drive hold the program on the drive and just updates the firmware or...
172
Hello everyone, I'm new here. First of all I just want to say that you guys are very knowledgeable and reading your posts on here has saved my...
176