We are using Powerflex 700 VFD to drive the starting motor of gas turbine. Reference speed signal to VFD comes from AB control logic PLC. When we give a start command to the turbine On crank mode PLC give a ref. speed of 36 Hz to VFD but VFD rotates the motor upto 12 Hz in 80 sec after that turbine stopped at fail to crank alarm. During running the out put voltage of VFD fluctuate. After reset of alarm we immediately give the second start command to turbine. This time the motor rotated upto 20 Hz in 80 sec after 80 sec turbine stopped on fail to crank alarm. During the second attempt the out put voltage and frequency increase smoothly upto 15 Hz with out any fluctuation above 15 Hz out put V/f again fluctuate. The parameter of VFD are same as when it was running normally. Kindly guide where is problem.
The parameter 238 fault config1 the share pin is disable. if the load on the motor is high what will be effect of overload on VFD drive.
It could be that there is some reason why the VFD is going into current limit mode. If that feature is enabled, the way a VFD controls current is to reduce speed, overriding the commanded speed. If speed fluctuates, voltage fluctuates because they go together. The way to test this theory is to locate that parameter that describes the action for current limiting and change it from reducing speed to faulting. Then try again and if it faults, you know that was the issue.
As to why it needs to limit current, it could be a mechanical issue or it could be a failing winding or motor lead conductor, failing phase to phase (because it would trip on ground fault otherwise).
Does anyone know off hand how to disable the start signal from a PowerFlex 20-HIM-A6? I've been looking through the manual but I'm not too...
1,544
I've got a Powerflex 700 that doesn't like to get going in the mornings. This motor will run anywhere from 30 seconds to 5 minutes before it just...
189
Looking for some assistance. I am very familiar with Yaskawa VFDs, but not so much with AB VFDs. I am working on some hardwired AB PowerFlex 700...
148
Can someone with Drive Executive please save me a printout of the parameters for this drive in this file. I'm in a bind and would greatly...
369
Hello all, I was forced to replace a Powerflex 700 to a Powerflex 70 due to what is available. The digital input parameters (361-366) have a...
492