PowerFlex 755 current change

oldnerd

Member
Join Date
Mar 2011
Location
Al
Posts
94
I have a powerflex 755 , every time the power is cycled on the drive the overload current changes from the setting of 1581 to 33. We have to go in and put the 1581 back in to get the motor to run..
Anyone know anything on this one?
I can not even find the parameter in the manual.
 
I have a powerflex 755 , every time the power is cycled on the drive the overload current changes from the setting of 1581 to 33. We have to go in and put the 1581 back in to get the motor to run..
Anyone know anything on this one?
I can not even find the parameter in the manual.
Is the VFD connected to a Logix PLC via Ethernet? If so, do you have ADC enabled? If so, then for some reason, you likely have the 33 value stored into the PLC memory for that IP address, so whenever power is cycled to the drive, ADC overwrites the values in the drive.
 
"ADC", in this context, is "Automatic Device Configuration", a technology that I really, really dislike for complex AC drives.

When the PLC connects to the drive, it reads the checksum for the writable parameters and compares it to its stored set. If they are different, it writes the stored value to the drive.

"ADR" and "ADC" are great for prox switches that get mashed by hammers, but I strongly prefer a reconfiguration / correlation function that requires judicial review for AC drives.
 

Similar Topics

We have 4 PowerFlex 755 drives that have been running for years. Each drive runs two motors. Recently, two of the eight motors began cogging at...
Replies
3
Views
736
Hi guys, We have PF 755 induction Flux vector control. When the drive stops the current doesn't drop to zero. It stays for 20 seconds. What...
Replies
6
Views
2,718
Hi All, I have a lifting/hoist application that I am using a powerflex 755 1hp drive. I am using a 1/3hp SEW gear motor that is rated at 0.57A...
Replies
3
Views
5,004
So I have a sort of unique situation where I'm wanting to run a PF755 from the IO and over ethernet. Of course, this comes with it's own set of...
Replies
9
Views
273
Hi I was wondering I need to update the firmware of a 755 inverter does the drive hold the program on the drive and just updates the firmware or...
Replies
5
Views
172
Back
Top Bottom