Premium IO mapping

KlausG

Member
Join Date
Apr 2010
Location
Cape Town
Posts
2
Hi
I would like to map %I0.3.1.0 for 64 inputs to %M500 - %M563.
What is the slick way of doing this. I have tried COPY_AREBOOL_AREBOOL
but I can't seem to get the syntax correct.

Any help would be great......
 
Hi
the following I did with UnityProXL v4.1.

The syntax would be %I0.3.0:63 on the input pin of the copy_arebool_arebool block and %M500:63 on the output.

Unity might give you the following error "E1200 usage of directly represented array variables is disabled"

this can be enabled under variables of your project settings.

hope this helps.
 
Thanks.....got it working. The default PLC %M was configuered
for Max 512 %M. It caused the addressing to stop at M512....my mistake

Thanks again
 

Similar Topics

Guys is there a method for mapping the inputs to a %MW address in a TSX Schneider Premium processor as a DINT? thanks hazey
Replies
2
Views
1,761
Everything was working fine, but suddenly CPU went into error mode, and the ERR and TER LEDs lit up. Now I can't download or connect with the PLC...
Replies
0
Views
63
Hello Dear Experts I have to read 2 words (%MW300 / %MW301) in a M221 plc (TM221ME16R/G) which have a embedded ethernet port. the reader plc...
Replies
4
Views
748
I have a asem premium hmi on a project we are working on. Just like a PV screen can do, i want to set a BOOL tag when a numeric input is...
Replies
1
Views
568
Hello All, I'm currently having issues getting a backup rack for a Modicon Premium TSX H5744M to function properly when it is brought online...
Replies
0
Views
1,139
Back
Top Bottom