problem in teleperm XP

eng_AJ

Member
Join Date
Jun 2010
Location
UAE
Posts
2
hi every one i wanna ask a question ,i'm I&C engineer in talkha power station made by siemens(V94.3A) and the control system is teleper XP(AS620B) , and we have a problem .
there are alarm on 12MBA12CP001 (signal fault ) but we look inside the telepermxp logic in the ES we found that the signal is ok ,and it read about 16.00 bar, so we try to restart the PU but the alarm does not rest so what can we do,
 
Remove fault

Hi
you should connect to PU whit rlogin and confirm the command:
Mv.Reset -sync FA (FA means function area)
 