Problem with Machine Edition upload from 90-30

NetNathan

Lifetime Supporting Member
Join Date
Nov 2011
Location
Corona, CA
Posts
2,199
I have an issue.
I am trying to resolve what logic is in a 90-30 PLC (364 CPU).
I have 3 Machine Edition backups with different names. All show Config=NE and logic=NE on Connect.
So... I did an upload, and it uploaded without error... but
it still shows Config=NE and logic=NE??
Validate is clean...
I have not stopped the CPU and tried yet... I guess that may be an option for fixing the Config error, but logic??

Any other ideas?
Running ME 10.2, and I am sure the older backups were from an older version of ME.
So I may have to even download the Config to clear error, but the logic issue bugs me.
 
If the program in the PLC was created with a different version of ME than what is on the connected PC, you will need to download to achieve logic or configuration equal status. Even if if you just uploaded.
You can run comparison report in ME to help set your mind at ease before downloading. It will flag any differences between the version on the PC and that in the PLC.
 

Similar Topics

Hello, I'm still pretty new at working with GE PLC. herei decide to start with asking just one question firstly. someone here can help out with...
Replies
0
Views
5,561
Dear all, The idea is I want to simulate 2 PLCs with the simulator and see if the runtime in the indus.PC changes. I have a PLC and SIS program...
Replies
0
Views
729
Hi guys! I'm trying to download a project to the controller, who already has an aplication running protected by a blank password. The option to...
Replies
3
Views
2,909
Hello! Im about to pull of all my hair over this: With this ladder i try to make a retained timer, with the possibility to reset it. But the...
Replies
23
Views
5,697
Hi everyone, I am beginner in the plc programming, and I am learning it using SoMachine basic software. There is a comparison command, which I...
Replies
4
Views
4,630
Back
Top Bottom