I have a problem with SLC 5/02 1746-L524 PLC of Allen-Bradley.It is a 10-slot rack with the following configuration.
Slot 0-CPU.
Slot 1-IA16 100/120 VAC.
Slot 2-OA16 (RLY) 240 VAC.
Slot 3-IA16 100/120 VAC.
Slot 4-OW16 Triac .
The PLC enters Fault mode and the LED keeps blinking ONLINE.
The error code in S:6 was 351h which means a "STUCK" runtime error exists on an I/O module and the error is non-recoverable.
We decided to download the same ladder logic on a brand new set of 5/02 chassis with new I/0 modules.Everything seemed perfect until we discovered the same problem ONLINE and the PLC entered the fault mode.
Both the set of 5/02 PLCs are now showing the dsame problem.
Where are we going wrong?
PLEASE HELP.